fuzzy



Joined: 29 Nov 2013
Posts: 672
Location: The Marches, UK

PostPosted: Thu Jan 11, 2018 3:38 pm    Post subject: Reply with quote

If I URL paste:

link here

it downloads to my PC

Of course you probably have to go searching to find where these things end up saving..

Interesting stuff, as you said BDU. Note the 75 GW 'total'
Back to top
View user's profile Send private message
kenneal - lagger
Site Admin


Joined: 20 Sep 2006
Posts: 10273
Location: Newbury, Berkshire

PostPosted: Thu Jan 11, 2018 4:27 pm    Post subject: Reply with quote

BritDownUnder wrote:
It's a spreadsheet. Very interesting too. Link below for you to tidy up.
DUKES_5.11.xls


I knocked it back to ww w.google.com...... and it worked OK.

Quote:
Who would have known that there was a 14MW power plant near a place in North Lincolnshire that burns "Meat and Bone Meal" as its fuel, in other words rendered slaughtered cows with suspected BSE!!!


BSE has gone completely as far as I'm aware. There is some testing done on older animals going into the food chain but there haven't been any instances reported in the press for a decade, at least, as far as I'm aware. It is probably just burning condemned animals and specified offal (spinal cords, etc).
_________________
"When the last tree is cut down, and the last river has been poisoned, and the last fish has been caught, Only then will you find out that you cannot eat money". --The Cree Indians
Back to top
View user's profile Send private message Send e-mail Visit poster's website
woodburner



Joined: 06 Apr 2009
Posts: 3660

PostPosted: Fri Jan 12, 2018 1:07 am    Post subject: Reply with quote

Post deleted as the link problem has been fixed.
_________________
Consensus guidelines are anti-science. Science is not about consensus.


Last edited by woodburner on Mon Feb 05, 2018 8:11 pm; edited 1 time in total
Back to top
View user's profile Send private message
kenneal - lagger
Site Admin


Joined: 20 Sep 2006
Posts: 10273
Location: Newbury, Berkshire

PostPosted: Fri Jan 12, 2018 4:16 pm    Post subject: Reply with quote

You wish is my command, WB (in this case only). Smile
_________________
"When the last tree is cut down, and the last river has been poisoned, and the last fish has been caught, Only then will you find out that you cannot eat money". --The Cree Indians
Back to top
View user's profile Send private message Send e-mail Visit poster's website
woodburner



Joined: 06 Apr 2009
Posts: 3660

PostPosted: Sat Jan 13, 2018 11:35 pm    Post subject: Reply with quote

Thank you KL, much appreciated.

To save KL extra work, you others please use the URL embedding tool in the line of buttons on the reply page.
_________________
Consensus guidelines are anti-science. Science is not about consensus.
Back to top
View user's profile Send private message
clv101
Site Admin


Joined: 24 Nov 2005
Posts: 7738

PostPosted: Sat Jan 13, 2018 11:46 pm    Post subject: Reply with quote

Just type it like this:

Code:
[url=http://www.example.com]Name of Page[/url]

_________________
PowerSwitch on Facebook | The Oil Drum | Twitter | Blog
Back to top
View user's profile Send private message Visit poster's website
kenneal - lagger
Site Admin


Joined: 20 Sep 2006
Posts: 10273
Location: Newbury, Berkshire

PostPosted: Sun Jan 14, 2018 5:33 pm    Post subject: Reply with quote

clv101 wrote:
Just type it like this:

Code:
[url=http://www.example.com]Name of Page[/url]


Now I've learned something as well. Thanks, Chris.

But you often have to leave the http:// off the URL.
_________________
"When the last tree is cut down, and the last river has been poisoned, and the last fish has been caught, Only then will you find out that you cannot eat money". --The Cree Indians
Back to top
View user's profile Send private message Send e-mail Visit poster's website
adam2
Site Admin


Joined: 02 Jul 2007
Posts: 6499
Location: North Somerset

PostPosted: Sun Feb 04, 2018 1:04 pm    Post subject: Reply with quote

Eggborough power station is to close before next winter.
Good news for the environment, but slightly concerning as regards UK energy security.
This closure wont affect available capacity for the rest of this winter, but is a potential concern for next winter.

I wonder what if any alternative capacity will be built.

The lost capacity is IIRC, about 2,000MW or about 4% of peak demand.

Our now very limited coal burning capacity has been regularly utilised, so unless peak demand is really going to drop by several percent in just one year, something else will be needed.
_________________
"Installers and owners of emergency diesels must assume that they will have to run for a week or more"
Back to top
View user's profile Send private message
adam2
Site Admin


Joined: 02 Jul 2007
Posts: 6499
Location: North Somerset

PostPosted: Mon Feb 05, 2018 7:56 pm    Post subject: Reply with quote

CCGT at 26.9 tonight which I suspect to be a new record.

It is I suppose reassuring that we have that much capacity.
OCGT also running, about 0.3. Demand is high at 48.8 but not exceptional, only a limited contribution from wind at 2.4, nuclear doing well at 7.4

Another night with an apparently small margin but during which the lights did not go out.

We could probably have coped with the loss of a couple of nukes, OR with the failure of half of the French interconnector, OR with a drop in wind to 1.0.
Had two of the above occurred it would have been interesting, and all three even more interesting.
_________________
"Installers and owners of emergency diesels must assume that they will have to run for a week or more"
Back to top
View user's profile Send private message
kenneal - lagger
Site Admin


Joined: 20 Sep 2006
Posts: 10273
Location: Newbury, Berkshire

PostPosted: Tue Feb 06, 2018 12:48 pm    Post subject: Reply with quote

Supposed to be very cold over the whole country tonight with low wind speeds so we'll see what happens then.

I'd better check the oil in my genny, I wouldn't want to have a power cut when the nation is OK. Wouldn't want a power cut at all really!
_________________
"When the last tree is cut down, and the last river has been poisoned, and the last fish has been caught, Only then will you find out that you cannot eat money". --The Cree Indians
Back to top
View user's profile Send private message Send e-mail Visit poster's website
adam2
Site Admin


Joined: 02 Jul 2007
Posts: 6499
Location: North Somerset

PostPosted: Tue Feb 27, 2018 3:52 pm    Post subject: Reply with quote

I expect electricity demand to be very high tonight and tomorrow night due to the cold, probably just over 50.
An actual shortage seems unlikely, unless SEVERAL things go wrong at the same time.
Wind is making a reasonable contribution at about 4
PV helps in daylight at about 3 but wont much help for the evening peak
Nuclear is doing reasonably at about 7
Coal is over 11, most unusual these days.
CCGT at about 20, low considering the weather. Another 5 should be available from gas if needed, but coal is being burnt in preference due to the high gas price.
We are exporting electricity to France which is somewhat unusual.

All figures in GW indicated on Gridwatch, other sources of data may differ.
_________________
"Installers and owners of emergency diesels must assume that they will have to run for a week or more"
Back to top
View user's profile Send private message
BritDownUnder



Joined: 21 Sep 2011
Posts: 347
Location: Hunter Valley, NSW, Australia

PostPosted: Tue Feb 27, 2018 10:01 pm    Post subject: Reply with quote

adam2 wrote:

We are exporting electricity to France which is somewhat unusual.

Probably very cold in France too - I hope they pay well for the power. Looks like all coal stations are on full power, the way it should be and keeping gas in reserve. Looked to be a fairly decent solar day too for winter. Wind seems to be holding at 5GW for now.

A slight change of subject but on the Fully Charged youtube channel there is an episode on a Scottish based maker of large megawatt scale heat pumps. Apparently they have sold one to Norway. I think the 'heat' is normally sourced from a river rather than air and the hot water produced is 90C and can be used in district heating/chilling schemes. I may put a post on the Geothermal section with a link when I am less busy.
_________________
G'Day cobber!
Back to top
View user's profile Send private message
RenewableCandy



Joined: 12 Sep 2007
Posts: 12563
Location: York

PostPosted: Tue Feb 27, 2018 11:47 pm    Post subject: Reply with quote

adam2 wrote:

PV helps in daylight at about 3

Had to lean out of the Velux this afternoon and knock the snow off ours Very Happy !
_________________
Soyez réaliste. Demandez l'impossible.
Stories
The Price of Time
Back to top
View user's profile Send private message
vtsnowedin



Joined: 07 Jan 2011
Posts: 4622
Location: New England ,Chelsea Vermont

PostPosted: Wed Feb 28, 2018 2:44 am    Post subject: Reply with quote

RenewableCandy wrote:
adam2 wrote:

PV helps in daylight at about 3

Had to lean out of the Velux this afternoon and knock the snow off ours Very Happy !

OK RC enlighten me, What to hell is a Velux? my best guess is a gable window but what do I know?
Back to top
View user's profile Send private message
adam2
Site Admin


Joined: 02 Jul 2007
Posts: 6499
Location: North Somerset

PostPosted: Wed Feb 28, 2018 3:55 am    Post subject: Reply with quote

"Velux" is a trade name for a popular brand of window that is intended for fitting into a pitched roof.
Commonly fitted to loft or attic areas when these are used for living space.

The term is often misused to refer to that style of window even if not made by Velux, other brands exist.

Not to be confused with "Vellux" which is a brand of blanket, made of nasty synthetic materials, easy to wash and durable, popular in hotels.
_________________
"Installers and owners of emergency diesels must assume that they will have to run for a week or more"
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    PowerSwitch Forum Index -> Electrical, Theory and Practice All times are GMT + 1 Hour
Goto page Previous  1, 2, 3 ... 8, 9, 10, 11, 12  Next
Page 9 of 12

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group